In a 3-phase power measurement by two wattmeter method the reading of one of the wattmeter was zero. The power factor of the load must be_______________?

Correct answer: B. 0.5

  • A. unity
  • B. 0.5
  • C. 0.3
  • D. zero

Explanation

In the two-wattmeter method, one reading becomes zero when the load angle is 60°, because one wattmeter measures a term proportional to cos(30° + 60°). Thus the power factor is cos 60° = 0.5.